Safety Relief Valves
Safety Relief Valves
(OP)
I have a safety relief valve on a water pipe tested to 200 psi being heated by steam at 525 F, 300 psi, and 6000 pph. I would like to determine the capacity and the pressure setting required for the valve. The safety valve will protect against thermal expansion of the water if the flow in the water pipe is stopped but is still being heated by the steam. Does anyone have a suggestion on how best to approach this problem.
RE: Safety Relief Valves
RE: Safety Relief Valves
RE: Safety Relief Valves
Use the common formulas for thermal expansion of water to size valve.
Thermal expansion is one thing - but what happen when the water starts to boil? Find latent heat at the SP (remember that the code allows a 21% overpressure for a single valve installation) and calculate steam flow at this P by use of your calculated duty and the latent heat. Redo the calculation for water but for the steam volume (the steam might accumulate somewhere and "push" water through the PSV.
Then there is the question of two phase flow... Since its a valve on a pipe this cannot be ruled out but im not familiar with two phase steam sizing sorry.
I think my methodology is somewhat on the conservative side -The duty when the water has stopped flowing will be lower. Usually in a "steam-heats-water" exchanger the major part of the thermal resistance will be on the water side. BUT i suggest you do the calculations - and if it dosnt mean a new (larger) valve then its not a problem and you _are_ on the conservative side. If it does mean a new valve go into more details.
Best Regards
Morten
RE: Safety Relief Valves
I will try to approch from total practical side. This problem is safety problem. Safety is the most important, all other things come after that.
1. Not only thermal expansion of water, but water pressure. When water expand thermally in this case its pressure rises because it is confined by pipe. The water pressure is what we need to control!
2. You must have some data for working pressure of water pipe. In this case you simply set safety relief valve to 1,1-1,15 x working pressure and that's it! Pressure must not come beyond it anyhow. But this is SECOND safety measure!
3. FIRST safety measure is: you must block steam inflow when water side pressure reaches some point that is above working pressure but bellow relief valve set pressure (let us say 1, 05 x water working pressure). This way real purpose of safety relief valve is to protect water pipe only from accumulated heat. It means when FIRST safety measure block the source of trouble (steam), there will be further water heating and pressure rise for a while because of thermal accumulation. This can be one moment or "little more", depending on water and steam volumes and contact area, but this moment is critical for safety because pressure still rises although you switch off everything
4. Not earlier then now thermal expansion comes into play. You calculate critical thermal expansion to find minimal opening area for relief valve. This is where you must consult standards. In my little country there is mandatory standard for this (it is called "Safety Relief Valve Calculation"; there must be some equivalent ANSI stuff).
Regards
RE: Safety Relief Valves
Usually you dont consider double jepordy - but i dont think that assuming that your safetysystem that should cut steam supply could fail when you have closed of the pipe with water is double jepordy. So you HAVE to consider the case where steam supply continue even though it SHOULD stop.
Best Regards
Morten
RE: Safety Relief Valves
I believe the code only allows the 121% of MAWP during a FIRE event. This would not apply, as there is no fire. The correct flowing pressure during relieving would be no more than 110% of MAWP. Of course, the set pressure of the PSV must be at or below 100% of MAWP.
RE: Safety Relief Valves
As for relieving capacity, I believe the ASME code has some information on how to perform these calculations, but I would contact the valve manufacturer and get their input. They designed the valves and given your parameters, they should be able to help you size you valve correctly.
RE: Safety Relief Valves
You are absolutely right when you say that failure of steam blockade must be considered. But this is what critical expansion calculation must take into account. Water evaporization must not start before relief valve begin opening (if that happens, THAT is the failure). What you want to avoid is explosion! If steam countinue to flow all the time (the worst case), only thing what can happen in any case is pipe wall overburn (which still must hold against rupture for the certain amount of time) because of decreased amount of water. This can be mitigated with adequte sizing of water volume ( as large as possible in critical area of effect).
One more thing: when that happens (steam blocade failure, which is not really often if double control system is mandatory like in my area) there must be an alarm as well which will warn people to escape as soon as they can.
RE: Safety Relief Valves
You are 100% correct 21% overpressure is ONLY for fire. Please note that there is an error in my first posting. its only 110%
Best Regards
Morten
RE: Safety Relief Valves
Im sorry i brough fire into the talk because its not about fire but about failure to close steam (on the hot side) when cold flow stops - a very likely situation.
I dont think steam formation in it self is a failure/catastrophe (at leat you got to elaborate on that) but the PSV must be sized to handle the three cases i described.
Best Regards
Morten
RE: Safety Relief Valves
RE: Safety Relief Valves
from Consolidated's catalog, section Thermal Expansion/API fire sizing.
GPM = BH / (500*GC)
where
GPM=Flow rate, in US gallons per minute at the flowing temperature
B=Cubical expansion coefficient per degree F for the liquid at the expected temperature differential.
water B=0.0001
H= Total heat transfer rate in BTU/hr.This should be taken as the maximum exchanger duty during operation.
G= Specific gravity referred to water=1.00 at 60F compressibility factor of liquid is usually ignored
C=Specific heat in BTU/lb?F of the trapped fluid.
Takeb from API RP 520 part 1
hope this will help
RE: Safety Relief Valves
When you have a PSV its something like this: Temperature remains constant bescause pressure remains constant (because "boil-of" is vented). For a HC system in theory temperature will rise because the composition changes but i wouldnt consider this.
If you didnt vent and kept a constant volume and kept adding energy (from the steam on the hot side) then the pressure would increase with the temperature. If the cold side is only water i assume that in the end it would evaporate when T_cold=T_hot because on the hot side its steam?
Best Regards
Morten
RE: Safety Relief Valves
RE: Safety Relief Valves
Thanks
RE: Safety Relief Valves
FCO, you may want to start a new thread with your question, or better yet, search for many excellent previous threads on this topic in the forums on this site. Check API 520 and 521 recommended practices, although you may have to buy these.
Good luck.