Working on a project, and the request is to move a Fisher H203 downstream of a 4" NPS 300# isolation valve on a natural gas pressure reducing station. I'm not sure yet what the logic behind the request is. Inlet pressure to the series-installed main and monitor regulators (both 600# rated) is 1035 psi. The Fisher H203 is located on a 1" branch just downstream of the main and monitor pressure regulators. Maximum set pressure on a 1" Fisher H203 is 300 psi, H203 valve body is rated for 400 psi. New set pressure on relief valve will be around 72-75 psi. If the working and monitor regulators fail, pressure upstream of the relief valve could start heading up towards maximum line pressure of 1034 psi. My concern is if the regulators fail, with the Fisher H203 moved to this new position downstream of the 4" isolator, if an operator closes that 4" NPS 300# isolator, the pipe flange and inlet valve flange at the isolator could be over-pressured, 300# flanges are good only to 749 psi operating. Any thoughts on this ? I think the H203 should be left where it is with new set pressure of 72-75 psi - or is the 400 psi body rating of the H203 (400 psi) a concern even though it's max spring (relief) setting is 300 psi ? It's tough to find these pop-type small relief valves with body ratings up to 1034 psi and the lower required set pressure of 72 psi. Just looking for 2nd views on this. Thanks.
The 2-stage reducing station doesn't work the way you think. The first stage valve, called 'monitor regulator' will take control of the total pressure reduction in case the second valve called 'active regulator' fails. ( see the two pilots that controls this valve vis-a-vis one pilot controlling the second or the active regulator). No matter which valve fails, you will get the final reduced pressure, which is 420 Kpag in your case. 420 Kpag (61 psig or 4.2 Barg) can be even taken by a 150# rated valve (1960 Kpag/19.6 Barg).
This should also explain why the d/s isolation valve rating of 300# is correct. This will be also your point of spec-break.
Typically, in this configuration the first/monitor valve will be 'fail close' while the second/active regulator valve will be ' fail open'. Also, the pressure reduction between the valves are typically shared. In our case,
1 st valve pressure reduction ratio = 1035 psig (7100 kpag)/348 psig(2400kpag) = 3:1
2nd valve pressure reduction ratio = 348 psig(2400kpag)/61 psig(420 Kpag) = 5.7:1
The PSV can be set at (420 Kpag +10%). It should be a full capacity valve. You can change this to a limited capacity that can be tied to a Safe Shut-Down valve (SSV) configured in the first monitor regulator valve that will stop the supply in the event the set pressure exceeds.
Check on the Fisher safety valve. You said Maximum set pressure on a 1" Fisher H203 is 300 psi. Your set pressure is @ 70 psig. it might be out of the setting range.
The original location of the safety valve is correct. Not sure why it has been commented to move it outside the d/s isolation valve. The piping between the two isolation valves must be protected from over-pressure (say due to temp rise in summer. This overpressure may rise fast depending on the location).