phamENG - Welcome to the profession!
Read AISC 303-16, the latest AISC “Code of Standard Practice”. Specifically, read Section 3. (It’s only a few pages.) If you have a 15th Edition AISC Manual of Steel Construction, you have AISC 303-16. If you don’t have the 15th Edition, you can download the COSP for free from the AISC website. You might want to show your boss this document. There have been some huge clarifications to the COSP since earlier editions. Two important points... First, there is more to delegating connection design than just delegating connection design. Second, if an EOR is involved in project where connection design was delegated, and where there was a connection failure, the EOR bears ultimate responsibility for that connection. Like it or not, that’s what it says (indirectly) in the COSP. There are articles and webinars available (at no cost to AISC members) on the AISC website that explain more. As more cities and jurisdictions adopt IBC 2018 (which references the 15th Edition AISC Manual, and AISC 303-16) it will become more and more important for EOR’s to understand the issues related to delegation of connection design, and the responsibilities of the EOR when doing so.