I am using the pretreated fresh air handling unit to dehumidify outside air for cooling.
I've designed the cooling coil with heat pipe wrap around.
My design figures for coil and heat pipe selection are as follows.
Air enters the heat pipe pre-cool section at 115/80 (DB/WB)deg F. After Pre-Cool (sensible free cooling only), air is at 95/75 (DB/WB).Then after cooling coil air comes out at 55/54 (DB/WB). and finally after the reheat of heat pipe (sensible heating), the air becomes 75/61.6 (DB/WB).
Sensible (free reheat)
My question is that, heat pipes removes sensible heat from the raw fresh air because of a refrigerant gets vopourized inside the pre-cool section. The amount of refrigerant vapourized (and hence the sensible cooling removed) depends upon the temperature of fresh air. Msx = 115 deg F
This fresh air temperature wont remains the same throughout the day. Now what will happen when the temperature of air comes down. will this heat pipe still able to pre-cool.
while selecting the heat pipe using a selection software or whatever, we never know what's the boiling temperature of refrigerant inside the heat pipe. which cause pre-cool and reheat.
I've designed the cooling coil with heat pipe wrap around.
My design figures for coil and heat pipe selection are as follows.
Air enters the heat pipe pre-cool section at 115/80 (DB/WB)deg F. After Pre-Cool (sensible free cooling only), air is at 95/75 (DB/WB).Then after cooling coil air comes out at 55/54 (DB/WB). and finally after the reheat of heat pipe (sensible heating), the air becomes 75/61.6 (DB/WB).
Sensible (free reheat)
My question is that, heat pipes removes sensible heat from the raw fresh air because of a refrigerant gets vopourized inside the pre-cool section. The amount of refrigerant vapourized (and hence the sensible cooling removed) depends upon the temperature of fresh air. Msx = 115 deg F
This fresh air temperature wont remains the same throughout the day. Now what will happen when the temperature of air comes down. will this heat pipe still able to pre-cool.
while selecting the heat pipe using a selection software or whatever, we never know what's the boiling temperature of refrigerant inside the heat pipe. which cause pre-cool and reheat.