Ampacity of a conductor?
It depends!
Here are some of the factors that determine rated ampacity;
Maximum temperature.
Conditions of use.
Duty cycle.
Wind speed.
Installers in Canada are governed by the following rule tables.
The bad news?
These tables are for field installations and do not cover panel building.
For that you must use a code to which I do not have access.
Canadian Electrical Code, Part I
302 © 2015 CSA Group
Table 1
Allowable ampacities for single unshielded copper
conductors, rated not more than 5000 V, in free air
(based on an ambient temperature of 30 °C*)
(See Rules 4-004, 4-006, 8-104, 12-2210, 12-2260, 26-142, 42-008, and 42-016 and
Tables 5A, 5B, and 19.)
Size,
AWG or kcmil
Allowable ampacity†
60 °C‡ 75 °C‡ 90 °C‡§ 110 °C‡ See Note (3) 125 °C‡ See Note (3) 200 °C‡ See Note (3)
Table 2
Allowable ampacities for not more than three copper conductors,
rated not more than 5000 V and unshielded, in raceway or cable
(based on an ambient temperature of 30 °C*)
(SIMILAR TEMPERATURE RANGES)
Table 5A
Correction factors applying to Tables 1, 2, 3, and 4 (ampacity
correction factors for ambient temperatures above 30 °C)
Table 5B
Correction factors for Tables 1 and 3 (where from two to
four single conductors are present and spaced less than
25% of the largest cable diameter)
Table 5D
Current rating correction factors where spacings are maintained
(in ventilated and ladder-type cable trays)
Table 12
Allowable ampacity of flexible copper conductor cord and equipment wire
(based on an ambient temperature of 30 °C)
Table 12A
Allowable ampacities for portable copper conductor power cables (amperes per conductor)
Table 12B
Temperature correction factor
(See Tables 12A and 12E.)
Table 12C
Conductor rating correction factor
(See Tables 12A and 12E.)
Table 12D
Layering correction factor
Table 12E
Allowable ampacities for Type DLO cables in
a permanent installation in cable tray
Table 28
Determining conductor sizes in the secondary circuits of motors
(See Rule 28-112.)
Classification of service
Percentage of nameplate current rating of motor
5-minute
rating
15-minute
rating
30- and 60-
minute rating
Continuous
rating
Short-time duty
Operating valves, raising or
lowering rolls, etc.
110 120 150 —
Intermittent duty
Freight and passenger elevators,
tool heads, pumps, drawbridges,
turntables, etc.
85 85 90 140
Periodic duty
Rolls, ore- and coal-handling
machines, etc.
85 90 95 140
Varying duty 110 120 150 200
Note: For motor-generator arc welders see Section 42.
Resistor duty classification Duty cycles
Carrying capacity of
conductors in per cent of full
load secondary circuit
Light starting duty 5 s on 75 s off 35%
Heavy starting duty 10 s on 70 s off 45%
Extra-heavy starting duty 15 s on 75 s off 55%
Light intermittent duty 15 s on 45 s off 65%
Medium intermittent duty 15 s on 30 s off 75%
Heavy intermittent duty 15 s on 15 s off 90%
Continuous duty Continuous duty 110%
Table 36A
Maximum allowable ampacity for aluminum
conductor neutral supported cables
Table 36B
Maximum allowable ampacity for copper
conductor neutral supported cables
Table 57
Allowable ampacities for Class 2 copper conductors
(based on an ambient temperature of 30 °C†)
Table 58
Ampacities of up to four insulated copper conductors in raceway
or cable for short-time-rated crane and hoist motors
(based on an ambient temperature of 30 °C)
Table 66
Ampacities of bare or covered conductors in free air, based
on 40 °C ambient, 80 °C total conductor temperature,
and 610 mm/s wind velocity
--------------------