Phlapjak (Electrical)(OP)11 Dec 23 19:22
You had already received numerous learned advice. I would like to add the following for your consideration.
1. In general, copper AWG 14 is fine. The current rating would be fine for (momentary only) closing/opening coil. Attention: in case use of low control voltage or with long distance, the voltage at the instance of coil operation, Shall > 0.85 rated operation voltage of the coil.
2. Irrespective whether the board is UL listed or in compliance with NEC, the 30A fuse is far too high for the copper AWG 14 conductor. The conductor is NOT protected irrespective whether it is energized momentarily, during operation.
3. Suggestion: Strongly recommend a) replacing the 30A fuse with a < 15A breaker attached with an auxiliary signaling contact, or a 2-pole breaker using 1-pole for open/trip signaling.
b) an un-noticed blown fuse on the trip coil circuit may result to very serious consequence, unless it is continuously monitored by a trip supervision relay.
Che Kuan Yau (Singapore)