Wind exposure category in mountains

Status
Not open for further replies.

McSEpllc

Structural
Feb 25, 2006
108
Hi Everyone,

Wind exposure categories per ASCE do not directly address mountains. I am working on a residential project on a mountain with a slope of 42 degrees. The mountain is wooded.

Surface roughness B: ...wooded areas...
Surface roughness D: ...unobstructed areas...

What would you use?

Thanks!



Eric McDonald, PE
McDonald Structural Engineering, PLLC
 
Replies continue below

Recommended for you

You must use the more stringent requirement if it is an interpretive issue. Check with the local building department....they might have some guidelines.
 
Thanks Ron - that is what I have been going with.

Eric McDonald, PE
McDonald Structural Engineering, PLLC
 
When designing a house on a 42 degree mountain slope, I'd not lose sleep over using a more conservative wind load...
 
You will probably find that this is a special wind region.
 