I have been going through some calculation sets where I have found in the longitudinal direction wind design the end condition values were overlooked. Is there a resonable explaination for ommiting these values on a MWFR building.
One explanation the engineer offered is that the building is flexible and the loads are being distributed in that manner.
The building has a frequency higher than 1 so the design is based on a ridgid structure, even at that if they did design it for a flexible building the end zones should not be ignored.
The calculations originated in Europe so perhaps the European code does not account for the End zones?