Calculor, welcome back.
Now another question - are you designing for ASD (Allowable stress design or Working stress design) for your design loads, or are you using LFD or LRFD?
If you are using LFD or LRFD, then I withdraw my comment about allowing for variation in the applied loads, since essentially the concerns that I would have should be met by a typical load combination of (for example) 0.9*Dead + 1.25 * wind.
However, if you are still designing on a 'working stress' basis, then I would still argue that you may not have sufficient allowance for variation of loads, since an increase in your uplift column load combined with a decrease in the column downward load could create significant negative bending (even without any coincident applied bending).
Note, the condition that I am thinking of is not the safety of the nominal 'working' condition, but the requirement to provide adequate reserve against an 'ultimate' load combination (either strength or stability), which may not be satisfied by simply using a factor of safety on nominal working stresses.
Adding appropriate top reinforcement could be needed to meet an ultimate load condition for strength in your footing, but of course would not have any effect on the stability factor.