What THD are you measuring, Voltage or Current?.
If it is voltage, you have a real problem and nothing much would be working right at your facility.
Assuming its the current, measuring harmoincs at no load of a motor is meaningless. You are analyzing magnetizing current which has very low (0.2 or less) power factor. 60% THD on no load means nothing. Please measure THD at full load, 75% and 50% loads which is a more meaningful analysis.
I do not know what THD the magnetizing current should read, But whatever it may be, I would not attach any singnificance to it,unless I see high THD in loaded condtion.
You may also wish to measure Voltage THD on the supply bus when the motor is off.