I'm sure it is known to all the participants, but I will mention that the energy storage characteristics of an inductor (Energy = 0.5 * L * i^2) are inextricably tied to the terminal characteristics (v = L di/dt).
Stored Energy = 0.5 * L * i^2
d/dt (Energy) = v i = 0.5 * L * d/dt(i^2)
Using the chain rule for differentiaion:d/dt(i^2)=2 i di/dt
v i = 0.5 * L * 2 i di/dt
Simplifying:
v = L di/dt
I didn't interpret David to state anything to the contrary. I heard him express an opinion that energy does not add much to the question of where does the energy come from. That is the same sentiment I expressed above.
When the voltage is removed from an induction coil, the DC current will continue for an easily calculated time. Is this not a form of stored energy?
Agreed 100%.
Scenario 1 - (waross' scenario) If you short out the voltage source of an inductor, the initial current will continue to flow and decay as the energy is disippated in the inductor. You will note in this type of transient, the current is never larger than the initial current.
Scenario 2 - The transient associted with worst case dc offset after a fault. The voltage accross the inductor INCREASES (it is not shorted to 0). The current flowing the inductor can INCREASE beyond the value that it had at the time of the short. It is a whole different transient.
The two scenario's have similarities. The similarity is that the energy associated with the dc comopnent decays away as it is dissipated in the circuit resistance giving a dc current of exp(-t*R/L).
The two scenario's have an important difference in terms of where the energy associated with the dc offset came from. In scenario 1 where I short out the votlage source, the energy came from the prefault circuit. In scenario 2 where I applied a fault, the energy associated with the dc offset was delivered into the circuit by the power suply within the first half cycle after the fault.
=====================================