Nayeem1993
Electrical
- May 31, 2024
- 13
Hi everyone.
We have 2 separate 110V DC system with separate FCBC charger and Ni-Cd battery.
system-01 powers 400kV main-01 protection with control(Close coil and Trip coil-01 of CB). System-02 powers main-02 protection(operates Trip coil-02 of same CB).
Recently we are facing a problem where if both chargers are running, then one of them automatically increases it's voltage at battery terminals(upto 154V)- even if the charger is kept in float mode. If only one charger is running then this problem does not happen. To check for any kind of unwanted interconnection between them, we disconnected one charger from system and connected a dummy load. The problem remained same.
What might be the reason? Did anyone face similiar problem?
Both battery and chargers are from HBL, India.
We have 2 separate 110V DC system with separate FCBC charger and Ni-Cd battery.
system-01 powers 400kV main-01 protection with control(Close coil and Trip coil-01 of CB). System-02 powers main-02 protection(operates Trip coil-02 of same CB).
Recently we are facing a problem where if both chargers are running, then one of them automatically increases it's voltage at battery terminals(upto 154V)- even if the charger is kept in float mode. If only one charger is running then this problem does not happen. To check for any kind of unwanted interconnection between them, we disconnected one charger from system and connected a dummy load. The problem remained same.
What might be the reason? Did anyone face similiar problem?
Both battery and chargers are from HBL, India.