Hello.
It is very simple, actually. But you have to look at the details of a sine wave. Like this:
1. A sine wave has two half-waves. One positive and one negative.
2. A short can occur any time (from 0 to 360 degrees) during the sine-wave cycle.
3. It can also be cleared any time during the cycle.
4. Now, let's assume that the fault happens at 0 degrees. Current will start rising in positive direction.
5. Let's also assume that the fault is cleared after 180 degrees (half a period).
6. If you draw the resulting wave-form on a paper, you will see a positive half-wave. Nothing more. No negative current.
7. The mean value of this positive half-wave is a positive DC current. That is how the DC component enters the scene.
Now, if the faults isn't cleared after 180 degrees, you still has that DC component in the system and it takes some time to get it out of the system. Typically up to 50 or 100 cycles in a large transformer and bolted short.
Look! No Math!
Gunnar Englund
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...