rhatcher; That is a 208 step-up to 380V to run part of the system. Just proving your point that the original system is indeed a 380V system. I also see your point about the 114Vac angle.
I saw the In-160 rating but the client states that the breaker is a 60A unit and we can't see the breaker handle in any picture. I'm guessing the In-160 is perhaps a model number or frame size?
He has no interest in running the saw slower, the VFD is simply to allow frequent starts. It was considerably less money than a soft starter that only allowed 5 starts an hour. He often has to stop the saw to make adjustments between each cut. The star-delta is dying and he hates it. As for the overload its setting should set the motor current with a stake-in-the-ground because it's never tripped at it's dial setting.
Isn't it wonderful how they feed the breaker AWG 6 THHN and then feed the delta contactor AWG 8 (55A @ 90C) for a so-called 18.5kW motor?
As for Jeff's idea:
I'm not clear on why the overloads would be set to 57% of FLA. So, for the moment, if I don't know why, I'm gonna bet the Chinese sure don't.
32A-20A = 12A
Estimating that the dial is about 70% of that 12A = 8A
20A + 8A = 28A
Remember 208V.
Well if that don't beat all..
A 28A 208V motor is less than 10HP!! What a rip-off.
Explains why the AWG 8 hasn't charred black.
It's looking like the VFD we have will actually work since a 10HP motor is a 7.5kW motor and the drive we have is an 11kW Drive. (I'll throttle back the overload setting.)
So if the 57% doesn't come back and bite us the uncharred wire and the (100%) overload setting all make this look like a 10hp motor regardless of its 18kW frame.
I'll put in the drive-in-hand and run it. With it working a load I'll read out the amperage the VFD is supplying. We'll go from there.
Keith Cress