I wanted to let you know what's transpired.
The drive-in-hand is an 11kW drive.
The Chinese motor was labeled 18.5kW.
The motor was mysteriously labeled 208V but is from 380V land.
Motor was originally installed with a now dying star-delta starter.
Yesterday we wired the motor in delta and dropped the leads onto to the possibly too small VFD that was in-hand. The manufacturer didn't bother running ANY grounds from the motor back to the control panel. Nor did they bother with providing a single ground point to the panel so none was brought by the 'electrician'. Cripes.
We tossed the drive on a piece of clean plywood on the floor and brought power from the YES 160A breaker in the panel, (Cripes
3), to the drive. Unlanded everything related to the S/D starter. Rewired the motor cables in the control panel on an existing terminal block to assure a delta motor connection. Landed jumpers from this to the drive output. Ran a ground thru the plastic chain guide (the motor travels). Landed it on a drive ground screw.
Ran a ground on the floor, out the door from the fused disconnect, out to the control panel. Ran a ground wire from the control panel to another ground screw on the drive.
Turned on the dead 160A (??!?!?) Chint breaker. Turned on the service panel 60A breaker feeding the disconnect. Cautiously applied power to the 160 via the illegally around-the-corner disconnect and the drive lit up.
Checked the max freq parameter. Made sure it was completely in 'FrontPanel' mode. No jog available... (weird) Set the speed to 4Hz and pressed run at arms-length. The saw gently started up and ran at 4Hz. We changed the display to current and it vacillated between 20A and 35A randomly. With it still displaying amps we increased speed up to 60Hz. At 60Hz the display went to a solid 20A. Interesting.
Left it run for 20 minutes. Motor rise about 2C. Air fanning out of the drive about 2C.
Hit stop. The drive tripped on decel over voltage. Don't need a controlled stop so reconfigured to coast-to-stop.
On current display started the saw. Saw 40A for one blink.
Hit stop.
Dropped a 12x14 piece of redwood on the saw. Fired up the mill controls. And ran some cuts while monitoring the current. His normal feed rate is 30%, we cranked it up to 80%. The maximum current reached in steady-state was 28A... Drive temp went up to about 5C, motor temp went up to about 5C rise. The drive seems adequate (47A rating).
Now to tidy-up the whole mess.
Thanks again for your great guidance in helping me thru this lying-plate madness.
Keith Cress
kcress -