Dear Mr jithin john
" ... squirrel cage 3 phase induction motor 415V ,585A ,1455 rpm coupled to a ... multi stage pump with h=320m,q=216m3/hr power 215kw ,rpm 1487 is tripping while starting the pump".
1. The motor 415V, 585A kW? is higher than the pump 215kW. Seems to be ok.
2. Please tell us a little more detail:
a) the power supply [measured] voltages [before starting] (i.e. L1-L2, L2-L3, L3-L1 and L1-N, L2-N, L3-N). If possible, also [during starting],
b) the starting method (i.e. Direct-on-line (DOL), Star-delta (S-D), auto-transformer (AT) etc. Note: unlikely DOL,
c) what is tripping (i.e. the breaker etc.. Note: if it is the [breaker], please show us the photo of the breaker (name-plate and settings). Does the breaker trips with lines to the motor removed (disconnected)? Does it trips [instantly] when starting; or after a some time say 3...10 seconds later? Or,
d) the [breaker] does not trip for some time say 10 seconds during (starting) but it trips [instantly] at the instant when changing over to (run),
e) if it is (S-D) starting, show us the control schematic diagram including the wiring from the starter to the connection on the motor terminals. Make sure that the [three links] on the motor terminals are [removed],
f) check and re-check that the wiring from the starter to the motor is per the schematic diagram,
As you are "mechanical", you may need some assistance from your "electrical" colleges to answer these questions. We standby to render our assistance at all times.
Che Kuan Yau (Singapore)