Welding to 1898 era steel 1

Status
Not open for further replies.

Engrman

Structural
Apr 2, 2002
54
A client wants to add canopies to his building. The canopies would be attaching to steel lintels supporting multi-wythe brick walls. The lintels consist of two 12"x20.5 'C' shapes with 3/8'' plates top & bot. According to historical records construction was completed in 1898. The earliest ASTM spec I can find is ASTM A9, dated 1900. It lists Fy=35 ksi and Fu=60 ksi for 'Medium' Steel. Should I spec 60xx welds?
 
Replies continue below

Recommended for you

Not knowing the weldability of the metal you will be working in the blind. Only if the forces are relatively small should one tackle the issue this way, I think. Are the plates of the Cs welded, or taken to angles with rivets?
 
ishvaaag, plates are riveted to flanges of C's. Lintel forms a box. Will be welding to web of C's
 
get a chemisty test done- it costs like $100 then you'll know exactly what to spec
 
Best to get coupons cut and tested for chem content. Some early stuff can be wrought iron or even cast iron. I can post a CE spreadsheet that I've put together for other projects.

Dik
 
A quick test is to weld a CS tab perpendicular (1 1/2 x 1 1/2") to the

web and try to break it off. Try a few licks the hard way and then bend

it off the easy way, it should break in the weld.

If you have and feel inclined here is a CS electrode (Cronotron 321, not SS) that I've used to weld some vary old and crappy steels, The welder will love it and probably take any leftovers home.


 
Dik, I would appreciate that spreadsheet. Thanks a bunch guys
 
The weldability can vary from one member to the next. They had no need to control carbon, sulfur, or phosphorous when everything was riveted.

You should have a chemical analysis performed on a sample of each member that is going to be welded to ensure the carbon equivalency is relatively low and the S and P are below 0.04% to minimize hot cracking problems.

You can deal with sulfur is you make sure the manganese content of the weld is 10 times higher than the sulfur content of the steel. I don’t know of an easy fix for excessive P other than to use low hydrogen practices, i.e., E7018 that has been stored in a heated electrode oven.


Best regards - Al
 
I would first be concerned about the condition of the lintel. In that age building, it may have significant corrosion.

Secondly, I agree that you need some chemical analysis to find out if it is weldable, but welding a tab to it and see if you can break it off will undoubtly tell you more.
 
jike, the lintel is in excellent condition. No corrosion anywhere. This is in a semi-arid enviroment. I agree with welding the tab.
 
Aside from the tab in my previous post there is an even quicker test, though much more severe. That is to weld a 1" dia (inside) circle using one or two circuits depending on how severe you want to be.

 
I've used nickel based electrodes for welding cast materials in past... I'll try to dig up a procedure.

Dik
 
I second the use of Hollo-Bolts; they work well. Many years ago I worked for an old timer - who started out in the 30's as a welder - he was adamantly opposed to welding to turn-of-the-century/early 20th C. steel. He would say it wasn't unusual to hit a carbon pocket and blow a hole in the steel.
 