JP20 said:
I decided to just use a W16x77 with lugs welded on top and bottom flanges in line with the webs. Kl/r for weak axis is 196. However this is a lot of determining factors in BTH manual that I still have to check. I did check welds earlier today and they are good being 8” long on both sides of lug - 1/2” fillet.
The choice of WF section will depend on load and span. You will probably need to comply with OSHA requirements for load factors. I am not familiar with them offhand, but I suspect they are higher than normal load factors for beam design for a building.
JP20 said:
This beam is going to be rated for 25 Tons of lifting.
If the span is 40' and the load is 25 tons or 50 kips, the maximum moment is 50*40/8 = 250ft-k.
But you told us something different in an earlier post:
JP20 said:
The max moment is actually more near 80ft-k .
JP20 said:
The part I hate most is that no matter what you do to this type of lifting device, you cannot laterally brace it. If someone knows of a way to, let me know! Otherwise I’ll be using BTH manual to design as 40’ unbraced.
If you use a span of 40', you will require a pretty hefty beam. Why don't you consider reducing the span by having a cantilever at each end? Not only do you reduce the span, but you apply a negative moment at each end which directly reduces the positive moment in the central span.
In a way, you are laterally bracing the beam at the pickup points by applying the load below the beam, preventing rotation about the beam axis. You could brace the top flange between pickup points with a top channel or plate, but it is probably more economical to select a WF which can span the central span without additional bracing.
The cables, chains or slings make an angle with the beam. They put moment and compression into the central span which needs to be taken into account.
Finally, if you feel uncertain about the design, I would strongly recommend that you retain an engineer familiar with this type of beam.
BA