Hello Buzzp
No, it is not the proximity of the earth return to the phase conductors that reduces the impedance, it is the surface area of the conductor. At 150KHz, most of the current flows in the outer 0.5mm of the conductor and nothing flows in the center.
If we take a standard circular conductor, at 50 Hz or 60Hz, the impedance is a function of the cross sectional area and length. At 150KHz, we could hollow out the enter of the conductor and leave a akin of say 1.5mm thick and the impedance would not change significantly, so per weight of copper, we want a thin conductor for minimum high frequency impedance. The screened cable is a low cost way of achieving a conductor with a high surface area for the return path.
I have solved numerous interference problems where the return path has taken a very different route than the phase conductors.
Issues that I have seen have been interference with the operation of flow meters and pressure transducers, I have seen numerous electromagnetic flow meters that have been damaged by the conducted noise currents. I have cured problems of interference with communications systems, radio and serial comms caused by the conducted emmisions.
I have not come across cable damage that I would associate with the output waveform of a VFD, but have seen motor failures that have been reported as first turn failures. More detailed analysis has shown this is not the case and have actually only seen two definite first turn failures due to VFD waveforms.
Bearing failure is a separate problem, once again the switching waveform causes currents to flow in the motor bearings via a number of different mechanisms.
The motor should be fitted with an insulated bearing at the non drive end, and a shaft brush at the drive end. There are different insulated bearing designs which have different results in reducing the bearing currents. Where the currents are inductively coupled, it is preferable to minimise the capacitance of the insulated bearing and in this case, the hybrid bearing is preferable.
A common mode choke on the output of the VFD will also help to reduce the bearing currents.
NB. This a separate problem from the conducted emissions interference issue, but it does also originate from the fast switching PWM waveform on the output of the VFD.
To minimise conducted emissions interference, you need a low impedance return path from the motor to the DC bus of the VFD.
To minimise bearing failure, you need an insulated non drive end bearing and a shaft grounding brush at the drive end.
A common mode choke on the output of the VFD is helpful in both cases.
To minimise the first turn failure in the motor windings, you need to limit the dv/dt applied to the cables at the drive end. This is best achieved with a true sinusoidal filter that provides common mode and differential mode sinusoidal filtering. dv/dt filters will act to reduce the transient voltage amplitudes.
Best regards,
Mark
Mark Empson
Advanced Motor Control Ltd