Do a search for SWER (single wire earth return) on this site or on Google.
Also check
I mention SWER specific because it is used (many parts of the world) in rural areas with a low population and density. Some advantages and disadvantages of SWER-systems:
Advantages
Simplicity - simple design allows speed in the construction of the system. No equalising of sags is necessary as in the case of 3phase
lines
Maintenance - Reduced maintenance cost, as the possibility of conductor-to-conductor fault on single-wire lines is removed
Low capital cost - Using only one conductor which results in longer span lengths, thus less structures and material
Metering - Load growth can be easily checked by inserting low-voltage instruments directly in the earth lead at the isolating transformer.
Voltage - A unique advantage of SWER is that there is a voltage rise of 1% to 2% at the receiving end (light loads only) instead of a
voltage drop whereas voltage drop invariably occurs in three-phase systems.
Power factor - not less than 0.9 to 0.95, the reason given that inductive loads are run in conjunction with static-phase converters which
make use of capacitors as one of the components.
Disadvantages
Single phase - supply only single phase
Conversion - The full advantage of the long design spans cannot be utilised if three-phase conversion is ever desirable. This is because
span lengths are optimised for a single conductor
Interferences on telephone lines - The system, when operating under high density load conditions, increase the degree of interference
with telephone and telegraph lines. If this necessitates conversion of telephone lines, considerable costs can be involved.
Earthing - System necessitates a periodic check on earth electrode resistance in order to ensure that no hazard exists from voltage
gradients across the surface of the ground.
Isolating transformer - Unit introduces additional system losses, construction and material cost.
Load balance of primary line - In common with all single-phase systems, the efficiency of the three-phase primary distribution line is
reduced when large loads are to be supplied. Max. load that can be supplied is largely dependent upon the ability of the three-phase
primary distributor to supply the unbalanced single-phase loading. This factor is the greatest disadvantage of SWER (and other single
phase) systems, but it can be overcome if arrangements are made to supply three SWER networks from a common point on the three-
phase distributor.
protection - protection against high impedance faults are difficult
From: An earthing design guide for SWER-systems in the Northern Cape region by C.H.L Sander
Regards
Ralph
[red]Failure seldom stops us, it is the fear for failure that stops us - Jack Lemmon[/red]