I am looking at a computer room with a 50 kVA UPS located within the room together with the aasociated batteries.
The UPS spec indicates a 40 kW maximum output (i assume the product of 50kVA and PF 0.8).
The computer room client is unable to provide a detailed listing of all of the equipment located within the room together with the associated heat output.
If the UPS is supplying power to various server based equipment what is the maximum heat load that could be expected???? (answering my own question assuming power in = heat out the maximum is 40 kW - does anyone have access to diversity figures?????????)
The UPS equipment will provide a heat output to the room (the tech spec does not indicate the amount) can a factor of say 10 - 20% be added to the UPS eletcrical output to estimate the approximate heat contributed to the space?
Will appreciate any comments.
The UPS spec indicates a 40 kW maximum output (i assume the product of 50kVA and PF 0.8).
The computer room client is unable to provide a detailed listing of all of the equipment located within the room together with the associated heat output.
If the UPS is supplying power to various server based equipment what is the maximum heat load that could be expected???? (answering my own question assuming power in = heat out the maximum is 40 kW - does anyone have access to diversity figures?????????)
The UPS equipment will provide a heat output to the room (the tech spec does not indicate the amount) can a factor of say 10 - 20% be added to the UPS eletcrical output to estimate the approximate heat contributed to the space?
Will appreciate any comments.