Hi
We have some motors 350 kW, 400 kW 690 Vac. We are a power plant exporting power on utility grid. Sometimes during disturbance on utility grid, our motors trip by under voltage.
These are critical motors so the whole plant trip resulting in penalties from the utility company. Motors are protected by Siemens Simocode. We already contacted Siemens. They recommended to reduce undervoltage setting. Problem is still occurring. The motors are boiler fans. They are started by soft starter with bypass contactor.
There is overload protection on the motors.
Undervoltage setting is 176 V 4s.
Can we disable the undervoltage protection? Is there any risk on doing this?
We have some motors 350 kW, 400 kW 690 Vac. We are a power plant exporting power on utility grid. Sometimes during disturbance on utility grid, our motors trip by under voltage.
These are critical motors so the whole plant trip resulting in penalties from the utility company. Motors are protected by Siemens Simocode. We already contacted Siemens. They recommended to reduce undervoltage setting. Problem is still occurring. The motors are boiler fans. They are started by soft starter with bypass contactor.
There is overload protection on the motors.
Undervoltage setting is 176 V 4s.
Can we disable the undervoltage protection? Is there any risk on doing this?