Mechanical
Mar 22, 2007
8
Hi, I am working to size a kitchen hood exhaust fan and have a simple question of air stream temperature recommended.

regards
 
Replies continue below

Recommended for you

Huh? For a house or a restaurant?

TTFN

FAQ731-376


 
Hi IrStuff

This is for a restaurant.

thanks
 
Actually, I guess I'm still confused, where in the overall air stream are you referring to?

TTFN

FAQ731-376


 
I think you will have to be a little more specific about what is under the hood.
Is this a hood over a range where you will need a grease duct, or is it over an area where only cooking pots for boiling vegetables are used, which does not require a grease duct?
B.E.
 
Normal Grease exhaust is about 110F - 140F. When selecting a fan, it is best to select a fan that has a max operating temp of at least 250F. This will allow the fan to operate in the event of a fire.

----
A green thought..."We don't inherit the earth from our ancestors, we borrow it from our children." (unknown)
 
To work it out find out the gas supply to the cookers, convert it to energy, and calculate the temperature rise using the kitchen exhaust rate.

Quick calc on a typical exhaust hood indicates about a 10 oC temperature rise.

This would be a worst case steady state scenario, but might be exceeded if there is a flare up when cooking.
 
Status