Hey,
I'm trying to get people's opinions on the proper way to call out additional reinforcement required for a two-way slab.
I've seen where its just called out as (11) #7 T (11 #7 bars at the top). The instance would be additional rebar over a column.
But should the EOR show how long these bars are, and at what spacing?
If the EOR doesn't, how does the steel detailer know? Just based on embedment length? The spacing?
Thanks