FreddyNurk said:UFRO only kicks in when the engine's rotating speed drops. There's generally (at least in anything that has an AVR) enough grunt to get at least 3 PU, usually greater at the instant of the fault. If the fault is close in and purely reactive then the engine won't slow down and the AVR will keep the excitation up, if its not then its slightly less predictable. I haven't seen too many incidents where it took 3-4 seconds to wait for the undervoltage to take a set out as compared to overcurrent on a fault.
If you're shutting down the engine, then its usually dropping speed as the fuel rack has gone back to zero fuel, and as a result, when the machine slows the UFRO still kicks in.
What I've said above is only based on my experience in high and medium speed diesel sets. Much larger sets will have different excitation arrangements, someone like ScottyUK has better coverage in that area.
It has been many years since I saw an electronic AVR that didn't have UFRO.OP said:The AVR would keep the voltage up
It depends.OP said:Will a short trip the generator breaker before stalling out? Will a close in fault still trip the breaker?
Compared to a transformer, not much after the initial transients.OP said:And that we are at it what is the available short circuit current of a typical 400-1,200kw genset?
With no charger other than the set driven alternator, eventually the battery fails and the set doesn't start.Mike said:Low water level in battery, level well below tops of plates.
....
A battery beyond its service life, corroded plates, sulfation, metal fatigue can all lead to internal arching that can lead to an explosion.