Waross said:I don't know, but in your position I may be moved to ask the ASCO rep, in writing, to be answered in writing;
How does the transfer switch perform in the event of the loss of one or two grid phases.
Given the very small clearances I am concerned about possible flashover in the event of an out of phase transfer when one pole of the switch is still hot on both sides.
Catserveng said:First off, here is a link to a nice and recent article about transfer switch types,
From my own experience, and I work on systems with ATS switches, multiple generators and critical systems all the time,
Feeding an ATS from another ATS is always a problem at some point. If the system is only going to be in place a few years you may get lucky, but if the system is really "critical", how much do you want to depend on that?
I would expect for you to get some really good answers first a bunch more questions need to be asked, such as,
Where is this system located, what codes must be followed?
Your drawings shows two utility sources and a bus tie, so does the system have both utilities in service and the tie open, or one utility service as primary, the other in backup and the tie normally closed? Has the timing of utility source transfer been accounted for in the ATS control timing sequences?
Does the "life safety" circuit actually involve life safety apparatus, and is it required to meet a 10 second (or as defined by local regulation) transfer time?
What kinds of loads are the "critical" ATS's feeding?
What kinds of loads are being fed from the three loads called "equipment" and what is their tolerance for not having redundancy in the emergency power supply?
Your drawing shows "Load Shed Controls" for Generator 2 but not for Generator 1 or no apparent interconnect between the two emergency sources controls, is that correct?
Have you accounted for the ability to perform regular maintenance, testing and repairs to the ATS switches, especially the ones connected to your "critical" loads? Are you planning on isolation bypass type ATS's? Or have you considered bypass maintenance circuits that allow you to completely isolate an ATS for service/repair?
Do you require Open or Closed Transition from generators back to utility? Do you require any form of load demand response, or the ability to do a closed transition transfer from utility to generators without load shedding or a system disturbance?
There are a large number of systems in service today with multiple generator emergency busses as David described above (at least in my area), and load shed/load add schemes to deal with starting and adding loads after the initial utility failure to being able to respond with the load shed scheme to drop loads if a generator fails while online.
How will you support regular testing of the generators? Do you plan on adding a spare (or defined load bank) breaker to each emergency bus? Do you plan on generator testing with site loads, or just dropping the generator leads and hooking up a load bank once in a while?
Have you developed a draft Sequence Of Operations for the power and emergency system first?
My 2.5 cents worth, hope that helps, MikeL