David Beach said:Weakest link in most emergency/standby systems is the ATS. The likelihood of a generator bus being unavailable while the normal source is out is far lower than the probability of an ATS failing.
Waross said:Yes. Allow both sets to start normally and to service their normal loads.
Speculation on the development of the control scheme:
1. The simplest solution, one generator and one transfer switch.
2. It was desired to service the critical loads and the life safety load with a dedicated generator. This may well be a regulatory requirement.
Solution: Two generators and two transfer switches.
3. While the generators had the capacity to service the loads, they would not support block loading of the entire loads.
Solution: Multiple transfer switches with staggered closing.
4. Someone in authority desired more redundancy on the critical and life safety circuits.
Solution: Install transfer switches to connect the critical and life safety load to the second generator in the event of the first generator failing. Note, these circuits have already been split to avoid 100% block loading. Hence three transfer switches are needed. This arrangement has the advantage that block loading of the second generator may be reduced by staggering the switch closures.
5. Issue. The combined loads now exceed the capacity of the second generator.
Solution: Install a load shedding panel. There are already multiple transfer switches on the second generator and these may be used to selectively drop feeders to free up capacity for the critical and life safety circuits.
And the last issue.
6. There may be an issue if generator #2 starts faster than generator #1.
Solution: Add a short time delay to ensure that generator one has enough time to come online before the transfer to Generator #2 is enabled.
With respect for David's suggestion.
That is a good solution for many industrial loads.
However I suspect that regulations in regards to critical and life safety circuits may have required the present scheme.
David Beach said:The data center I'm most familiar with, and not my design, starts four generators to carry a load normally supportable by two generators. All parallel into the load using the normal in-house distribution system. The design obviously assumed the probable need for the generation was loss of utility service. Once all four are up to temperature with no issues the lowest priority unit is shut down; now three carrying the load that two could carry. If one of the three fails the fourth is restarted to replace the failed unit. If the load ever gets down low enough that only one would be sufficient to carry it the lowest priority unit of the three running is shut down leaving two.
If you want to account for the possibility of internal cable failures, rather than just utility loss of supply events, you need to push the supply redundancy as close to the load as possible. Using ATSes that could mean a whole lot more than what you've shown. More ATSes, more single points of failure; fewer ATSes, a different set of more single points of failure.
Does loss of supply to a single ATS represent a failure of the system between a common point and the ATS or does it represent a fault downstream of the ATS that will also trip the standby source once it connects?
There may not be a single "right" answer. For a single building facility, loss of utility supply is probably more likely than loss of supply to a single ATS. For a multi building campus the odds of loss of supply to a single ATS increase. Approaches for each will differ.