I have several thoughts.
Yes, it should be possible to run the attic trusses out to the front dormer walls. But as Lexpatrie noted, it could be a problem a you get closer to the eaves at the dormer. You need height in order to get the attic truss to work. If the height above the wall (or heel height) and pitch are low, some of them may not work.
Cost could be an issue. As you likely know, it costs a lot more to make one of anything that it does to make several identical ones. If you step the TC up, you'd have maybe 10 or 12 unique trusses. Some pieces would match between setups, but not all. That would slow down the plant, and I'm sure they would charge accordingly.
It might be possible to extended the B.C. out to the bearing. It depends on what species and grades of lumber are available to the truss manufacturer.
I saw that you mentioned a 30# live load on the attic floor. I never design with less than 40# on any floor. I don't care what the code says. I think it allows for floor embers to be designed in ways that will make them under-perform.
Running attic trusses across a stair opening is a problem. You can't just cut the BC out anywhere you want to. The B.C. is in tension, and that has to be resolved.
Opinions on that vary from one manufacturer to another. Yours might refuse to do it, or they might be more accommodating.
I noticed your layout calls for the attic trusses to be 16" O.C. There's really no reason for that. It just adds a lot of trusses, and will likely make the job cost 40% more. (A rough number)
Is there a reason why the attic room is not as wide to the left of the stairs?
One final thought - I usually don't make rooms 16' 0" on attic trusses. (Unless the customer insists) The face of T&G plywood is something like 47 3/8". So I make the room 15' 10". That way they don't have a narrow strip to fill in.
Hope some of that helps.