I have always specified the attached detail when I have an architect want trusses to span more than about 35ft and ground snow loads are greater than or equal to 25psf. I haven't ever been questioned on it until recently when a contractor was all up in arms (not surprising). When calculating the point load from a truss on the double top plate, the double top plate fails in bending when the truss bears greater than 3" from the adjacent stud as shown on the detail. Are you guys providing this detail?
The argument I would make against it is that the dbl top plate would have to bend the plywood as well in order to fail. What are your thoughts?
The argument I would make against it is that the dbl top plate would have to bend the plywood as well in order to fail. What are your thoughts?