Is there a way I can bank transformers for wye-wye 3phase service with 120V phase to phase? This is for a special application.
Yes, it is possible. Two ways to obtain secondary voltage close to 120V phase-to-phase is as follow:
1-Order special three-phase transformer with 120 V in the secondary.
2- Use standard transformer with taps rated for twice the primary voltage. Operate the transformer connected to a primary voltage half the transformer rating. Automatically the secondary voltage will be half.
For example, if a secondary delta connection is allowed, choose a transformer with rated for 240 V phase to phase. The resultant voltage will be around 120V phase-to-phase.
If a YG is require the secondary voltage will be 104 V. In this case, the transformer tap should be increased as high as possible to obtaing a sec voltage closes to 120 V