I am a structural engineer and I would like to know if there is a calculation that translates the peak dynamic motion of a large HVAC unit to an equivalent static force for simplification. Or, do HVAC suppliers, such as Trane, have data available for the engineer's use?

-rob
 
No there isn't, as such. Once you know the input impedance of the building at that point then you can work out the force for a given displacment.


Note that the impedance varies with frequency, and a maximum displacement of the source doesn't tell you anything about the frequency content.