To install black start generator for 2 power generators 45 MW
SA07
MU
Hi
We have 2 turbo alternators 45 MW 11 kV 50 Hz each exporting to the utility grid. We intend to install a stand by generator to do black start of a turbo alternator in case of total black out of the national grid and then export some MW on the grid.
The auxiliary consumption of one plant before synchronising is about 2 MW.
We have a series of 11 kV circuit breakers next to each other for each unit and a common busbar as shown in the attached doc. After each unit are synchronised with the network, we want the std by generator to export some power to the grid.
Our biggest single motor is the boiler feed pump of 1 MW.
What rating of std by generator do we need? Will a 5 MW be enough?
Then after synchronising both units, will we be able to export an additional of 5 MW on the grid?
Is there a 5MW 11 kV std by generator on the market?
There is a request from the national grid company to increase our production because of some issues on the grid.
For a DG set to have black start capability, its auxiliaries should be minimum and / or should be able to start on DC battery.
I am afraid 5MW could be large to be able to start on its own. You may discuss this with a reputed manufacturer before making a decision.
Since the black start power requirement is 2MW only, a 2.5 or 3MW set could be good enough. To cater to the starting power requirement of BFP, the generator alone can be of higher MVA rating. This is because 1MW motor may take 5MVA power during start @ a power factor of 0.2 (say). This is to say a DG set comprising 3MW Diesel Engine and 5MVA Generator.
Optionally, if a Soft starter can be added to the 1MW motor, the starting current can be limited to 2x the rated current.
What is the energy source of the proposed standby generator?
If diesel powered, you probably can't afford the fuel to export power.
Size the standby to black start the most demanding power generator.
After starting one or both power generators, leave the standby online and advance the frequency setting until it is exporting the load that you desire.
Governor droop will cause the frequency setting to control the loading for export.
For a diesel set exporting power, make prior arrangements with your banker before refueling.
Black start is an emergency for which hydro generators and GTG's are more suited than STG's which take anywhere from 10 to 18 hours to synchronize.
My recommendation is Install a PQ meter and trend your plant load during startup. Your standby set will only need to carry the load until one of the 45MW generators sync and begins to share the load.
There’s a chance that a 2.5MW generator would work because your aux loads might relatively low during startup, but the only way to determine that is to measure.
We blackstart a 75 MW gas turbine site with a 2 MW gen, but the aux loads on gas turbines are relatively small other than the .5MW starting motor.
In my region (Washington state, USA) the emissions limits for emergency generators are much less stringent (tier 2) than for generators intended to export power to the grid (tier 4). It extremely rare for folks in my area to buy a tier 4 engine for an emergency generator, so we could not legally sell power from an emergency generator to the market. Other regions have very different rules. I think Minnesota has a utility sponsored programs to run customer owned emergency generators at peak demand times.