Hi
We have 2 turbo alternators 45 MW 11 kV 50 Hz each exporting to the utility grid. We intend to install a stand by generator to do black start of a turbo alternator in case of total black out of the national grid and then export some MW on the grid.
The auxiliary consumption of one plant before synchronising is about 2 MW.
We have a series of 11 kV circuit breakers next to each other for each unit and a common busbar as shown in the attached doc. After each unit are synchronised with the network, we want the std by generator to export some power to the grid.
Our biggest single motor is the boiler feed pump of 1 MW.
What rating of std by generator do we need? Will a 5 MW be enough?
Then after synchronising both units, will we be able to export an additional of 5 MW on the grid?
Is there a 5MW 11 kV std by generator on the market?
There is a request from the national grid company to increase our production because of some issues on the grid.
We have 2 turbo alternators 45 MW 11 kV 50 Hz each exporting to the utility grid. We intend to install a stand by generator to do black start of a turbo alternator in case of total black out of the national grid and then export some MW on the grid.
The auxiliary consumption of one plant before synchronising is about 2 MW.
We have a series of 11 kV circuit breakers next to each other for each unit and a common busbar as shown in the attached doc. After each unit are synchronised with the network, we want the std by generator to export some power to the grid.
Our biggest single motor is the boiler feed pump of 1 MW.
What rating of std by generator do we need? Will a 5 MW be enough?
Then after synchronising both units, will we be able to export an additional of 5 MW on the grid?
Is there a 5MW 11 kV std by generator on the market?
There is a request from the national grid company to increase our production because of some issues on the grid.