As I kept reading and re-reading this thread I kept thinking:
If you are up against the VFD current limit, you are also at an HP limit.
You need more HP.
If the maximum current is fixed, then for more HP you will need more voltage.
Then I found this:
Does the VSD supply input voltage have an effect on the output current? The actual voltage is 388 V instead of 400 Vac.
The current limit is also a torque limit.
Higher voltage will result in greater HP.
But that greater HP will be in the form of higher speed at the same torque.
In order to take advantage of the greater HP you will have to change the fan curve by either trimming the impeller or by restrickting the discharge.
Some thoughts:
We haven't mentioned density or temperature.
Testing with the boiler stopped the flow will be cooler and more dense putting more load on the motor at a given speed.
Testing with the boiler stopped the there will be no fly-ash and the flow will be less dense.
Conclusion; testing with the boiler off-line may not be a valid test.
Solution:
Determine the maximum allowable supply voltage of the VFD.
Consult with the fan designers.
Real world data is not agreeing with the curves.
This may be caused by a greater flow density than the design assumptions.
It is not the fault of the designers if you operate their fan outside of the design parameters.
The best attitude is:
"FIX THE PROBLEM, NOT THE BLAME."
Share your operating data (Values when the boiler is in operation, not off-line) and request assistance.
They should be able to suggest a combination of motor speed and fan modifications that will allow you to take advantage of the full HP of the motor.
You and the fan designers should be working to a torque limit, not a HP limit.
At nameplate current, a motor supplied with over voltage and over current may safely develop more than nameplate HP.
I suggest doing calculations based on 440 Volts if the VFD will accept that.
This will give you a 10% increase over nameplate speed and nameplate HP.
Ask the fan designers for suggested modifications to the fan so as to be able to use that HP at that speed.