Wear off of the fan tips does the same thing as trimming the OD of the wheel.
If speed is held constant the fan curve moves inward.
If shaft speed is increased so that fan wheel tip speed is the same as new then performance will be similar to new.
In this case wear off of the fan wheel tips makes it possible to run the fan a bit faster before fully loading the motor (Amps = Nameplate FLA). While you might be able to run into the service factor (Amps = Nameplate FLA*S.F.) at nameplate speed, you are operating at a lower speed so the cooling air moving through the motor is less than design, this risks shortening the motor life.
The fan OEM should be able to provide a set of fan curves showing fan OD vs head and flow at motor nameplate speed (I am assuming the blower is direct connected to the motor). The best selection would be one that fully loads the motor at nameplate speed (Amps = Nameplate FLA). If the motor is fully loaded (Amps = Nameplate FLA) at less than name plate speed you are running in the service factor. and power (Watts) is significantly lower than nameplate.
Posting the fan curve for you current configuration will result in better answers here.
This might not really be a problem with either the fan, motor or VFD, Large industrial boiler systems are a rather complex system problem, where troubleshooting requires steeping back from the immediate problem, and looking at how the observed problem relates to other parts of the plant.
The described situation can be caused by incorrect setting of fan inlet air spin (
ie incorrect setting of inlet guide vanes or dampers, or perhaps a baffle near the fan inlet is loose or out of position. This situation is highly dependent on duct layout and damper position - upstream vs downstream of the fan.
The described situation can also be the result of excessive restriction in the dust collection system (damper set more closed than it should be, stopped up cyclones or blinded bags, incorrect coordination in the control system between dampers and fan speed control).
Do you have a record of how this fan operated when the plant was commissioned? If it ran at design speed and a reasonable motor load, look for what might be different now vs when the plant was commissioned.
Fred