Does anyone have any tips on designing timber trench shoring. This should be easy, but I am missing something. The method of shoring the contractor has proposed is with vertical wood planking which are 3X8 or 4x6 douglas fir with a bending strength of 1500 psi. The system consistes of these vertical planks with wales and 2 struts, wales and struts are located 3' from the bottom of the pit and 2' from the top. I analyized the verticals like a simple beam with the struts as rollers and the retained soil as the loading, but I can not get any of the proposed sizes to work, even though the contractor has had the system reviewed in another state and it worked, basically I am recertifing for my state.
I even found tables here saying these memebers should work
I think OSHA has some standard details and tables on shoring- you might check for comparison.
Could you be figuring soil loads more conservatively than what the tabulated values assume?
the link I included shows the OSHA table and there loads are what I am basing my calcs off of. I even called OSHA about where they found there values, but they could not even find the table, not much help from them.
ahhh, details details, sorry about that, the trench varries from 5'to 20' deep and is pretty much set a 8' wide. Another thing to add in is that the water table is varies also.
thank you for the CA shoring manual that looks like a great starting point. I have to say the CA DOT always has great resources.