well im learning one thing from this forum. how easily one small statement can get turned all around.
here is a quote from the fluke document i was referring to
"Output side measurements
Measurements on the output
side of a pulse width modulated
(pwm) motor drive have been
difficult or impossible to make,
especially accurate measurements,
that would agree with
the drive controller displayed
values. The traditional true rms
multimeter will not provide accurate
answers. This is because
the voltage applied to the motor
terminals by the VFD is a pulse
width modulated non-sinusoidal
voltage.
A true-rms DMM will give
an accurate reading of the heating
effect of the non-sinusoidal
voltage applied to the motor, but
will not agree with the motor
controller’s output voltage reading
which is displaying the
rms value of the fundamental
component only (typically from
30 Hz to 60 Hz). The issues are
bandwidth and shielding. Many
of today’s true rms digital multimeters
have a wide bandwidth,
sometimes out as far as 20 kHz
or more, which allows the meter
to respond not only to the fundamental
component that the
motor really responds to, but also
to all of the high frequency components
generated by the pwm
drive.
In addition, if the dmm is
not shielded for high frequency
noise, this can also lead to poor
measurement performance due to
the high noise levels generated
by the drive controller. Because
of their higher bandwidth and
shielding issues, many true rms
meters will display readings as
much as 20 to 30 % higher than
the drive controller is indicating.
Fluke’s new 289 multimeter,
with it’s ¼ VGA dot matrix display,
has the ability to display
multiple parameters at the same
time and utilize the selectable
low pass filter, giving the troubleshooter
or engineer the ability
make accurate voltage, current
and frequency measurements
on the output side of the drive
either at the drive itself or at the
motor terminals and also display
the filtered output voltage and
frequency (motor speed) simultaneously.
With the filter selected,
the 289 readings for both voltage
and frequency (motor speed)
should now agree with the
associated drive control display
indications if they are available.
When measuring output current
with a clamp accessory, the low
pass filter allows for accurate
current measurements and frequency
measurements simultaneously
when using the Hall-effect
type clamps. All of these measurements
are especially helpful
when making measurements
at the motor location when the
drives displays are not in view"
all i said was that fluke stated this meter would do this. if it wont then fine flukes information is obviously misleading.
i would like to thank you for making my first experiance in this forum so enjoyable! i will seriously consider any input i may have in the future.\
a simple reply of "in some cases the built in filter will take good readings but in many instances the filter is not sufficient." would have been nice.
but if you must ingnore the explanation of why i gave the statement i made and instead point out things in my response saying well if you said this you must be a moron. By all means have at it...