"...Never seen it in any of the motors I have handled. Also, 65kA for 1 sec? For motors?"
1. I think this is the "general" Basic data template. This template could be a "cut-and paste" in their procurement document. We encounter these flaws very often.
2. I agreed there are flaws:
a) Under installation location
690V 60Hz is unlikely, as 690V is widely used only in the IEC 50Hz locations.
b) 65kA 1s is referring to the short circuit level at the installation location, which is possible/likely. It is NOT in the Motor performance basic data column.
3. For my knowledge, for LV <1kV motors, do you perform Dielectric test voltage at 2kV 50/60Hz 1 min. in your shop, or in your geographical region ?
Che Kuan Yau (Singapore)