'tis like this:
A motor that big has very little resistance in its windings. As you know, it is electrically equivalent to a (rather bad) transformer.
So, the current is roughly U/X, where X is the winding's reactance (omega*L).
Now, if there is more magnetization than the system can take, i.e. saturation, the X goes to zero and the current rises beyond normal values. A lot beyond. Also, there is a lot of 0 rad/s (DC, that is) and that is only limited by the near zero R in the circuit.
The very high current heats thyristors and fuses and starts to trip breakers. If the thyristor i^2*t is less than that of the fuse - which is alewys the case if standard fuses are used - then the thyristor either melts down or evaporates before fuse cuts out. Usually the first. Breaker usually takes longer time, so it trips a little while after.
I had a similar experience a couple of years ago and the recordings from that event are interesting. See attached file.
Gunnar Englund
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...