Sulfuric Acid Storage
nicolai
NA
Hi Folks
possible to direct me to the applicable codes and guidelines regarding bulk outdoor storage of Sulfuric Acid (98%)
many thanks
1. Are you in the USA?
2. Do you have a code or standard you have to meet?
3. Type of container, average quantity per container
Thks cdafd
application is bulk storage 50m³
what code in the NFPA suite is most applicable ?
many thanks
Explain why your question was posted in the "NFPA fire Code Issues" forum ?
Will you be using Sulfuric Acid in fire protection in some way ???
MJCronin
Sr. Process Engineer
Thks MJcronin
I want to establish the good practice and regulations regarding the storage of bulk sulfuric acid from an fire prevention & protection perspective
Thanks LCREP
is did reviewed FM 7-111F
they dont mention any special fire measure like sprinklers for bulk storage tanks ( i.e 50 m³)
perhaps not a prerequisite for sulfuric acid
my concern is overpressure and subsequent release in case of fire
I think section 2.4.5.2 regarding vacuum breakers, hydrogen gas detection and high level alarms are definitely things to consider. Again they are trying to limit a loss $$ by early intervention.
yes indeed - thks a lot
I take this is not in the USA?
Suggest get a Fire Protection Engineer that deals with Hazardous Materials
There is to many questions, to get a good answer here