You haven't really provided enough information. What are the loads? How much of the loads are shear, compression, or tension on the joint? Width of gap? Number of bolts? etc. Sketches tell a lot of information. A significant amount of shear on a joint with a filler gap greater than 1/4" can significantly reduce the bolt shear capacity. PTFE is not a structural filler, it is only used in film thickness for expansion joints.
SathGayu said:
Use of metal (slopped washers) will be the best solution but it will be a very time consuming.
Why not steel finger shims? These are approved by AISC and are used regularly after joints have already been erected. AISC 360-05 spec. section J5 explains limits on fillers and the joint shear strength reduction as a result. These are contingent on structural steel plate filler material. I guess if the joint is mainly in bearing and the loads are fairly low compared to the joint capacity, you could look into using a solid fabric pad such as those from Fabreeka
Link. But, I would not try to use them in combination with AISC spec J5.
Again, depending on the joint and the severity of gap, another option could be groove welding the perimeter of the open faying surfaces. In that case, the loads (shear, axial, moment) would have to be taken by the welds, as welds and bolts cannot be used in combination since their load-deformation curves (stiffness) are so different from each other.
"It is imperative Cunth doesn't get his hands on those codes."