Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Strange sound in centrifugal? 1

Status
Not open for further replies.

DOX638

Industrial
Joined
Feb 3, 2004
Messages
1
Location
US
Hi'
I have a 2 stage carrier centrifugal 3000ton(17fa599/drive murray turbine)
Over the summer it developed a muffled "sound".
vibration analsis,alignment and refigerant sample were taken.turbine bearings/thrust were ALSO inspected.
All were within limits except refrigerant(water was found/500ppm). The oil cooler was leaking and is in the process of being repaired along with reclaiming the charge.
Would 500ppm/water cause a compressor to sound different,with no lose in capacity or exccesive head press.? Also what would be an acceptable ppm of water in the charge?


Thank you, I appreciate your comments.

 
To illustrate the range of values among refrigerant types, at 40 degrees Fahrenheit, R-11, R-123 and R-134a will become fully saturated at the following levels:

CFC-11 - 44 ppm

HCFC-123 - 470 ppm

HFC 134a - 600 ppm

so looking at these perameters it's very possible that with 500 ppm the total chemistry change in your refrigerant could very well created sound you were hearing.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top