NewbieStruct
Structural
- May 31, 2011
- 101
I have a situation where a joist girder sits on a WT that is welded to embed on an existing tilt panel wall. Does the embed take only shear? My senior engineer says since everything is attached, the deck, the joist are in place the connection will only take shear. I feel that the joist girder load will cause an eccentric load on the WT and therefore induce moment on the embed. We are planning to increase the capacity of the floor deck for the building and the general loading will increase by 10 psf. If I account for eccentric load the existing embed fails. If the connection is pure shear it is ok. If I need to design for moment, how should I tackle the problem?