How deep is the embedment? Is this into a foundation wall, a floor slab or a stand alone foundation?
Personally in the case of a floor slab, I don't check for shear unless it's a very high shear load. Essentially the load would have to break out a good section of floor in order to be of concern. In the case of a stand alone beam, I design exactly as if it were the end of a concrete beam (stirrups for shear down the foundation, anchor bolts treated as for top and bottom bars analysed as per reinforcing for a beam. With a foundation wall, I combine the two (so long as I have a good load path) since parallel to the wall it is like the floor slab case, and perpendicular to the wall it only works if the base is connected into the floor diaphragm.
I do hope I have correctly interpreted your question!
Regards,
YS
B.Eng (Carleton)
Working in New Zealand, thinking of my snow covered home...