Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

star point

Status
Not open for further replies.

vavavoom

Electrical
Joined
Aug 26, 2005
Messages
1
Location
GB
my boss has just informed me that if the earth( ground) is connected to star point it will potentially become live is this true

 
Live Earth? That would be a new one; ground (earth) is the reference voltage, anything solidly connected to ground is at zero volts. If there is current flow in the connection, there will be a voltage drop between the point measured and ground, but ground is still at zero.
 
Connecting the starpoint of a transformer, generator et.c. to ground is giving you a TN- or TT- system (the first T means solidly grounded neutralpoint). The other letter is determining how your PE-conductor goes.

If the neutral is not connected to ground, you would have a floating neutral, i.e. an IT-system.

:)

tm
 
Aside: 'T' comes from the Latin word for 'earth', Terra.


----------------------------------

One day my ship will come in.
But with my luck, I'll be at the airport!
 
Astute point ScottyUK! I was just thinking why "T"!?!?

You are clairvoyant.[spin]
 
Status
Not open for further replies.