Actually, leaving out VFDs because that is totally different, reduced voltage starting does not fundamentally change the “thermal pain” for an AC induction motor. The area of the curve for the energy it requires to accelerate a given load is the same no matter what. The only thing RV starting does is to trade the height of the curve for the width. I have argued in the past that stretching out the time allows more of that thermal energy to be dissipated during the acceleration process, but someone pointed out that the thermal resistivity of a motor is so high that it makes almost no real difference if it takes 2 seconds or 30 seconds to accelerate.
This issue came up in discussions as to whether using RV starting can allow an increase in the number of starts-per-hour a motor is capable of. There was a camp who said it did, because it lowered the peak current and thereby the peak heat, others felt that stretching out the start time caused MORE heat in the motor. The answer was what I said above, that the energy curve area is exactly the same size, so the answer is no. It doesn’t help, nor hinder.
Reduced voltage starting has only two benefits; reducing excess torque applied to a load that doesn’t need it, and reducing current when the supply is limited. I cannot imagine a situation where the 3 phase supply is unable to handle the starting current if a 3kW motor, and centrifugal fans are very easy to accelerate, so I can’t see starting torque as being an issue.