Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

snow load on design of foundations

Status
Not open for further replies.

EITCanada

Structural
Joined
Oct 23, 2001
Messages
2
Location
CA
hello,

for design of FOUNDATIONS, should all the snow drifts be considered? or could i take a simplistic approach of considering an uniform average snow load?
the building in question is only one storey high.

thank you very much
 
Snow drifting can be quite significant at times and we usually include it in our foundation design. You can, however, use approximate loads and areas in your calcs instead of using an extremely precise calculation.
 
Where it is customary to establish an allowable pressure on the soil as in Spain, the limit states combinations don't contribute much to the (unstated to such purpose) safe or probabilistical establishement of service level loads from which the actual pressure is to be got for comparison, so I understand your question. So on the one hand I understand some approximation would be here possible, since the code itself is undefined, but as well one has always to consider any situation that is likely to occur, in which case drift could become critical sometime somewhere.
 