I would have to agree with TD2K. I have specified sloped steam piping, only to be laughed at by construction management and contractors. When you hear an old timer pipe fitter say that he has never, in his 20 years of installing pipe, installed a sloped steam line. You wonder what is really going on out there. I have gone back and made pipers slope lines that are on roller type clevis hangers, but with welded shoe type bottom support, this can't be done too easily.
The truth is that sloping steam piping is the correct way to do things. However, in actual application this may not happen. The best way to make sure that you don't have a water hammer event is to drip trap your mains. I have read a rule of thumb for drips is one every 200' for piping sloping in the direction of flow and 100' for piping sloping against flow. A drip at a riser will take the place of one of these drips. I put a trap every 100' just to cover myself.
This is a case of engineers knowing the correct way something should be done and the field doesn't believe that it is important. Cover yourself. It might cost a little more, but unless you get a contractor you can work with, you need to make sure your design is a good one.