I am getting back into a project that has been on the shelf for some time. One room of a water supply building has six large filter tanks that will periodically be drained. We have a trench system and 8" D.I. floor drain but the area of floor one which the tanks sit is flat.
The frost walls extend 2' above the finished floor in this part of the building so there can be no overpour or shelf. I think it makes sense to take advantage of this and reduce the restraint on the slab by using smooth dowels instead of deformed to provide transfer of vertical forces but not lateral, like a cold joint within the slab. I have not seen this done but I do not see why it could not be.
The question is whether or not a fiberboard or similar iso joint is necessary at the perimeter. While I want to prevent bond, I think the slab will only contract away from the wall. Also - I need a strip of bentonite as backwashing those filters will result in a huge amount of water on that floor - fiberboard, or even poly sheet, will prevent that from working. Has anyone seen a simple chemical bond breaker or release agent used effectively at cold joints? It would be cleaner (no gap- architect would be happy), allow waterstop to do its job, unless there is a chemical rxn issue (not to mention not interfere with dowels). I know this detail is a little unusual, but I dont see why it will not perform very well. Let me know if you have concerns or issues.
Thanks
I am getting back into a project that has been on the shelf for some time. One room of a water supply building has six large filter tanks that will periodically be drained. We have a trench system and 8" D.I. floor drain but the area of floor one which the tanks sit is flat.
The frost walls extend 2' above the finished floor in this part of the building so there can be no overpour or shelf. I think it makes sense to take advantage of this and reduce the restraint on the slab by using smooth dowels instead of deformed to provide transfer of vertical forces but not lateral, like a cold joint within the slab. I have not seen this done but I do not see why it could not be.
The question is whether or not a fiberboard or similar iso joint is necessary at the perimeter. While I want to prevent bond, I think the slab will only contract away from the wall. Also - I need a strip of bentonite as backwashing those filters will result in a huge amount of water on that floor - fiberboard, or even poly sheet, will prevent that from working. Has anyone seen a simple chemical bond breaker or release agent used effectively at cold joints? It would be cleaner (no gap- architect would be happy), allow waterstop to do its job, unless there is a chemical rxn issue (not to mention not interfere with dowels). I know this detail is a little unusual, but I dont see why it will not perform very well. Let me know if you have concerns or issues.