I am replicating a project that was originally done in SKM about 4 yrs ago and I am using EasyPower Ver 9.5. There are some differences in conductor impedances but nothing major. I have found one item that is curious. For this particular panel:
SKM: HRC 0, 1.2 cal/cm^2, Ibf 16.06kA, Iarc 8.35 kA, Trip time 0.044 sec
EasyPower: HRC 1, 2.4 cal/cm^2, Ibf 16.4 kA, Iarc 8.515 k, Trip Time 0.086 sec
The protective device is a Siemens Sentron NXD6 1200A breaker with a 1200A trip and Inst at 5000A. Now what is interesting is when the TCC is plotted, SKM's Iarc current would result in a trip time of ~0.091 sec. When I cross a trip time of 0.044 on the curve, the corresponding current is ~12.4 kA.
This is at 480V, 60hz system
Any thoughts or comments? -
SKM: HRC 0, 1.2 cal/cm^2, Ibf 16.06kA, Iarc 8.35 kA, Trip time 0.044 sec
EasyPower: HRC 1, 2.4 cal/cm^2, Ibf 16.4 kA, Iarc 8.515 k, Trip Time 0.086 sec
The protective device is a Siemens Sentron NXD6 1200A breaker with a 1200A trip and Inst at 5000A. Now what is interesting is when the TCC is plotted, SKM's Iarc current would result in a trip time of ~0.091 sec. When I cross a trip time of 0.044 on the curve, the corresponding current is ~12.4 kA.
This is at 480V, 60hz system
Any thoughts or comments? -